GFCI resets at the outlet but still fails — what are we missing?

We keep running into the same one on HUD inspections: a GFCI outlet in a kitchen or bath that trips and resets fine at the outlet, the little test button clicks, the light comes back on — and the inspector still marks it as failed.

What we have learned to check before we call it done: press the test button, confirm power actually drops at that outlet and at every outlet downstream of it, then reset and confirm power comes back everywhere downstream too. A GFCI that only protects itself, or one wired so a downstream outlet stays live when it trips, is not doing the job. We also check that it is actually a GFCI where one is required, not a standard outlet someone swapped in, and that the cover and box are sound.

It is a five-minute check with a plug-in tester, and it has saved us from a failed inspection more than once. The outlet looking fine is not the same as the outlet working.

How do you test GFCIs on your turns — test button only, plug-in tester, or both?
 
One distinction worth adding for readers: another socket nearby isn't necessarily supplied through that GFCI's protected load side. The intended protection needs to be established before treating a socket that stays live as proof this device failed.

Leviton's instructions distinguish line and load arrangements and describe checking the connected outlets. For a failed or uncertain result, have a qualified electrician verify the configuration and protection rather than opening the outlet or changing connections as a trial. Record the specific sockets checked so the next visit doesn't start from guesswork.
 
Good distinction — nearby does not always mean downstream. Before I call a socket a failure, I need to know whether it was meant to be protected through that GFCI's load side in the first place.

That is why I record the specific sockets I checked, and what happened at each one when the GFCI tripped, rather than writing 'GFCI checked'. The next visit then starts from a clear record, not guesswork.

For a failed or uncertain result, I do not open the outlet or change connections as a trial — a qualified electrician verifies the configuration and the protection.

Do you find more GFCIs that protect only themselves, or more where a downstream socket stays live when it should not?
 